Just wondering what kind of cooling tower temperature drop to expect when cooling tower is operating with all the fans off and no evaporative cooling. If water at 450 gpm @ 95 deg F (from chiller condenser) enters cooling tower water distribution on the coldest winter day say -20 deg C dry bulb, what kind of temperature drop is expected. I'm designing a cooling tower by-pass line to divert some of the cooling water return (going back to the tower) to go directly into the chiller condenser when outisde temperature is very low.
|
Cooling Tower Load W/chiller Operation
Started by toronto engineer, Oct 09 2007 09:17 PM
2 replies to this topic
Share this topic:
#1
Posted 09 October 2007 - 09:17 PM
#2
Posted 10 October 2007 - 07:48 AM
I would contact the cooling tower vendor. You will need to know the model, fill type, etc.
Just get a few things straight: it is usually not a good idea to mix up your units of measurement. Either use gpm and deg. F or m3/h and deg. C.
Also, you need to know the wet bulb temperature when you rate a cooling tower. There will always be evaporative cooling when there is water flowing in contact with air, and that is what drives the performance of the tower.
Isn't there a problem with freezing up the tower when you reduce the water flow? Minus 20 deg. C sounds awfully low.
Just get a few things straight: it is usually not a good idea to mix up your units of measurement. Either use gpm and deg. F or m3/h and deg. C.
Also, you need to know the wet bulb temperature when you rate a cooling tower. There will always be evaporative cooling when there is water flowing in contact with air, and that is what drives the performance of the tower.
Isn't there a problem with freezing up the tower when you reduce the water flow? Minus 20 deg. C sounds awfully low.
#3
Posted 11 October 2007 - 11:27 AM
Dear,
Here are some articles in the following journals related to your query,
http://www3.intersci...n...=1&SRETRY=0
http://www.sciencedi...0a4d14104aeb5e0
And a very useful article on Coolin water is availabe here in Cheresources and a DOS programm for
the cooling tower calculations,
http://www.cheresour...ctowerszz.shtml
As well the same query is discussed in the forums below
http://www.eng-tips....d=184967&page=7
I hope that it will help you.
Regards,
Padmakar Katre
Here are some articles in the following journals related to your query,
http://www3.intersci...n...=1&SRETRY=0
http://www.sciencedi...0a4d14104aeb5e0
And a very useful article on Coolin water is availabe here in Cheresources and a DOS programm for
the cooling tower calculations,
http://www.cheresour...ctowerszz.shtml
As well the same query is discussed in the forums below
http://www.eng-tips....d=184967&page=7
I hope that it will help you.
Regards,
Padmakar Katre
Similar Topics
Aspen Custom Model Won't Load Into HysysStarted by Guest_SaintLazarus_* , 21 Mar 2024 |
|
|
||
Psv Fire Case Relief Load CalculationStarted by Guest_mahmooddalvi09_* , 21 Feb 2024 |
|
|
||
Minimum Tower DiameterStarted by Guest_AnbIran_* , 17 Nov 2023 |
|
|
||
Sizing Of Cooling Water Pipe LineStarted by Guest_Asif Azeez_* , 08 Jan 2021 |
|
|
||
Heating And Cooling Circuit DesignStarted by Guest_AAZIZ_* , 20 Jan 2024 |
|
|