Air Consumption
#1
Posted 11 July 2008 - 06:48 AM
I need a firm figure from you all. I am carrying out air consumption calculation for our small project. I have three control valves and three pneumatic on/off valves. My doubt is i could not get the air consumption figure for each control valves; more over is it continuous requirement or just at a time of actuation?
Two nos. of controlvalve for steam application with sizes 50NB and one no. controlvalve for water application with size 65NB.
Plz reply....
#2
Posted 11 July 2008 - 03:33 PM
I am attaching a small excel sheet which gives an estimation for air consumption of various types of pneumatically operated instruments. Please note that although practically in a steady state operation there is no actual consumption the table attached tries to quantify air consumption on a continuous volume flow basis.
The tabular numbers have been picked up from some company guidelines and please do not ask me to reveal the source since revealing the source is a breach of confidentiality. As an abundant precaution, I have mentioned that the air consumption for any particular type of instrument should be verified with the instrument manufacturer/supplier.
Regards,
Ankur.
Quick note from the admin: This attachment is so good, we've moved it to our File Library
Edited by Chris Haslego, 19 November 2012 - 02:14 PM.
Moved to File Library
#3
Posted 12 August 2008 - 09:22 PM
#4
Posted 12 August 2008 - 11:55 PM
The link below has excellent tips on receiver sizing.
http://www.pyebarker...ps/techtip3.htm
#5
Posted 13 August 2008 - 12:03 AM
As I have very categorically mentioned, the air consumption for any instrument has to be ultimately verified by the instrument supplier/manufacturer. Most reputed control valve vendors such as Fischer, Valtek and others will be definitely able to provide the maximum air consumption if asked. The spreadsheet that I have provided encompasses some broad guidelines based on some company standards. No details about the exact mode of air consumption is provided such as leakage or any other mode. However, you are free to use whatever data has been provided to you if it concurs with the manufacturers recommndations for air consumption.
Hope this helps.
Regards,
Ankur
#6
Posted 13 August 2008 - 01:29 AM
the air consumption for control valves is different and a function of:
1-supplier
2-valve system
3-line pressure
4-work conditions
in 1-3 items the rate of consumption is constant but in 4th item, the variation in work conditions is a factor of air consumptin.
on/off valves need continuously air pressure and no air consumption(except a little consumption due to leakege) and in air flow disconnection, the position of valve will set to normal position that its depend on that the valve is normal close or normal open.
therefor you need to talk to your supplier.
cheers
#7
Posted 14 August 2008 - 08:18 AM
Please do not use maximum because we will get oversize consumption.
Just use the steady state consumption + 20 % contingency. It will enough. For easy calculation you may state that each control valve consume 1 SCFM (vendor usually give less than this value in steady state consumtion, but it's still OK).
Best regards,
Rizaldi
#8
Posted 19 August 2008 - 03:58 AM
Actually now this has become an issue for me. I could not get authentic data which is suppose to be given by vendors. Different vendors giving different data considering higher size marzin. I dnt want to oversize my compressor at all.
we have been taking 7 Nm3/hr so far but it is apparantly seem so high. Let me give u some inputs which is given to me by vendor. May be others can throw more light now.
I got following data from vendor
For control valve,
1.4 bar pressure
0.15m3/hr for 6mm tubing, 0.225m3/hr 8mm tubing, 0.45m3/hr with 12mm tubing.
for 6 bar pressure
0.5m3/hr -6mm tubing, 0.75m3/hr-8mm tubing, 1.5m3/hr-12mm tubing
Above is what exactly vendor has given me in mail. From this now i have to assume lot many things.
firstly i assumed that he is talking flow at specified pressure not but Nm3/hr
second, 1.4bar pressure he must be referring after Air regulator
Does anybody have a familier feeling with these figures, is it seem ok?
to be continued....
#9
Posted 20 August 2008 - 08:12 AM
Would you be kind enough to tell us, which vendor has provide the data.
I am a little surprised that the vendor has given the consumption based on air tubing size. Is the consumption based on leakage by rupture of the tubing?
As far as consumption in m3/h is concerned that seems justifiable since air is to be supplied at some pressure to the pneumatically operated diaphragm of the valve. The 1.4 barg and 6 barg seem to be the minimum and maximum pressure limits for operation of the control valve diaphragm.
As I undertsand, the volume of the pneumatic cylinder/diaphragm of a on-off/control valve play a role in determining the air consumption. For a full stroke of the control valve (0 to 100%) opening for an air-to-open control valve the volume of air required to fill the pneumatic diaphragm can be found out. With some reasonable assumption of the maximum number of strokes that can occur in a unit time period (say one hour), the volumetric flow rate can thus be determined.
Have you checked out with some reputed vendors like Fischer (Emerson), Valtek, Masoneilan for air consumption for your type of control valve. I would tend to believe some of these internationally known vendors than some local vendors who have been duplicating design of international vendors without having the thorough knowledge and insight of control valve engineering.
As a summary, I fail to understand your insistence on exact numbers for air consumption for the following reasons:
1. If as an exact calculation you have determined that your total air consumption is X Nm3/h, it is highly unlikely that an air compressor vendor would be able to supply you a compressor with your exact requirement of X Nm3/h. Air compressor vendors nowadays, have standard packages with a combination of flow rate and pressure and designated as model numbers. No air compressor vendor offers of-the-shelf compressor as per the customers exact calculations for air consumption. Essentia;lly it means that if the air compressor vendor has one model which gives a flow rate of 1.15X Nm3/h and the next lower model which gives 0.9X Nm3/h, you are not going to get into an argument asking him for a model with the exact flow rate of X Nm3/h. The most sensible thing I would do is just go ahead and buy the model with the flow rate of 1.15X Nm3/h.
2. If you look at the vendor catalogs of air compressor vendors, many a times two different model numbers (numbers close to each other) having small difference in flow rates and the same discharge pressure have the same motor rating which ensures that your OPEX remains the same between these model numbers.
Personally, I feel the topic has no merit for further discussion based on my above points for air compressor selection.
Regards,
Ankur.
#10
Posted 20 August 2008 - 11:19 PM
let me tell you why i am insisting the air flow consumption for control valve, actually we devide the total air consumption in two different classes continuous and non continuous and we size the compressor based on continuous requirement, for non continuous we size air receiver so as to cater peak requirement which is for small time. Now i consider air bleeding across control valve is continuous requirement and when we talk about 50-60 nos. control valve in whole plant, it becomes substatial figure. We have been taking it as 7Nm3/hr but i found it should be nearly 2-3 Nm3/hr, now you can emagine if my latter finding is true and when there are 50 nos. control valve, imagine how oversize my compressor would be.
Now as far as compressor selection is concern, i agree that i cant get the compressor exactly of my size, rather i would select next higher size, but in above case it becomes substantially oversize, which i would not accept.
neways, you are right, it's not benificial enough to stretch this topic anymore. let us close the discussion.
And once again thanks a lot to all for your valuable inputs.
#11
Posted 21 August 2008 - 01:51 AM
Dear Jiten Process,
Pardon me for entering into the discussion, but I feel like adding my little comments as follows gathered from my almost 28 years stay at my previous employer 3 refineries complex mainly Pnematic intruments/Control valves and many a times witnessed problems during rotating shifts.
Hope the above helps.
Best regards for all colleauges as these healthy arguments open hidden facts for everyone's awareness indeed.
Qalander
#12
Posted 30 March 2011 - 02:51 AM
In your exel file above what's your standard reference conditions of temperature and pressure?? Is the reference temperature 0 degr.F/15degr.F/20degr.F etc.?? Of course i know the pressure is usually 1 atm..
#13
Posted 30 March 2011 - 08:57 AM
SCFM / Sm3/h refers to a condition of 60 deg F (15.56 deg C) and the pressure is 1 atm abs (1.01325 bara)
Hope this clarifies.
Regards,
Ankur.
#14
Posted 07 September 2011 - 02:06 AM
It will be so kind of you, if you can please tell me the exact procedure of calculating the air consumption rate of control valve (both for on/off and throttling).
Best Regards,
Shakeel Khattak
#15
Posted 07 September 2011 - 06:27 AM
The procedure as such is not very simple since it involves the volume of the cylinder / diaphragm for the on-off / control valves, the time-cycle (frequency) of operation of the valve as well as the leakage rate from the cyclinder / diaphragm. Here only one factor is easily determinable which is the cylinder / diaphragm volume with the other two very difficult to estimate.
The excel sheet provided in this post gives fairly conservative figures for air consumption and one could always provide a safety factor on the calculated air consumption so that the instrument air package is not undersized and may even be able to take care of future modifications / debottlenecking of the plant. Shell, for example recommends a contigency factor of 1.3 on the calculated air consumption.
I don't see the need to do such detailed calculations based on the procedure I have mentioned above. I would consider it a luxury to spend time on such detailed calculations.
Regards,
Ankur.
#16
Posted 20 February 2012 - 11:18 AM
Can u provide me information for Pneumatic valves working on basis of solenoid valve.
#17
Posted 20 February 2012 - 11:53 AM
Any pneumatic valve has either a diaphragm or cylinder system for actuator movement. Solenoids only energize and de-energize to facilitate either supply of air or venting of air. I don't see what difference a solenoid is going to make on the air consumption of a pneumatically operated control or on-off valve.
In case you are so particular about obtaining exact values of air consumption as a flow rate then the best way is to get the information from the manufacturer / vendor of the pneumatic valve. Otherwise, a conservative estimate (higher consumption figure) is fairly acceptable.
Regards,
Ankur.
#18
Posted 21 February 2012 - 01:07 AM
- I agree to and fully endorse Ankur's above comments.
#19
Posted 25 August 2012 - 03:10 AM
Thanks lot for the detail information provided in this forum.
Similar Topics
Centrifugal Pump In Recycle Mode: Constant Power Consumption But FluctStarted by Guest_Kakka_* , 23 Jan 2025 |
|
![]() |
||
Need Help Understanding Increased Power Consumption In Injection PumpStarted by Guest_Kakka_* , 21 Feb 2025 |
|
![]() |
||
Variables That Affect Energy Consumption Of Methanol PlantStarted by Guest_mobody_* , 15 May 2024 |
|
![]() |
||
![]() Maintenance And Power ConsumptionStarted by Guest_Lyne_* , 04 May 2024 |
|
![]() |
||
Air Consumption For On Off ValvesStarted by Guest_itsmetinnie_* , 11 Mar 2024 |
|
![]() |