Dear all,
What is the basis for control valve sizing for a hydrocarbon containg vessel with split range pressure control? To elaborate, the vessel is under nitrogen padding with split range pressure control system. If the vessel pressure is less than set pressure, vent control valve will close and nitrogen inlet valve will open to put more nitrogen inside vessel. If vessel pressure is higher than set pressure, nitrogen inlet valve will close and vent valve will open to vent the excess vapor/gases and vessel will get depressured to set value.
Now my questen is, how to size the inlet and vent cotrol valve? Any guidelines available?
For more clarity refer attached sketch.
Piyush,
Sizing from process view-point will involve the following data to be generated:
1. Flow Rate:
a. The inert gas feed valve flow rate will be based on the inbreathing (liquid outflow + thermal inbreathing ).
b. The vent valve feed rate will be based on the outbreathing (liquid inflow + thermal outbreathing).
Inbreathing & outbreathing calculations can be done according to venting calculations as given API 2000 or alternatively I have made a post for tank venting calculations in the Relief Device sub-forum which can be utilized for doing the same calculations:
http://www.cheresour...?showtopic=73272. Pressure Drop:
a. Minimum pressure drop: This will correspond to the pressure difference betwen the min N2 operating pressure at the valve inlet and the maximum operating pressure of your vessel.
b. Maximum Pressure drop: This will correspond to the maximum N2 operating pressure at the valve inlet and the minimum operating pressure of your vessel.
Other data provided by process for sizing the valve is the fluid, it's physical properties (specific gravity, viscosity) and its critical properties.
All the above mentioned data when provided to the control valve vendor/manufacturer will enable the vendor/manufacturer to size the valve.
Regards,
Ankur.