Vortex Breaker


This topic has been archived. This means that you cannot reply to this topic.
6 replies to this topic
Share this topic:
| More

#1 chemicalkannan

chemicalkannan

    Junior Member

  • Members
  • 14 posts

Posted 07 April 2009 - 11:31 PM

Hi Friends

am Working in EPC Company.Currently We are doing Crude oil Tank Farm Projects. in this Project am doing Detail Engineering.my dought is The PMC is mentioned Data sheet ,the necessity of vortex breaker is determined by detailed engineering contractor.how can i find the vortex breaker is required or not.

by
kannan

#2 JoeWong

JoeWong

    Gold Member

  • ChE Plus Subscriber
  • 1,223 posts

Posted 08 April 2009 - 12:14 AM

kannan,
A liquid exit from a nozzle and the liquid height (between liquid surface and nozzle/hole) is below a minimum submergence height (S), free surface vortex potentially form and vapor entrainment into liquid outlet is possible. Vortex break is required. You need to determine the minimum submergence height. There are many article discussing this topic. Check out "Minimum submergence to avoid vapor entrainment"


#3 Zauberberg

Zauberberg

    Gold Member

  • ChE Plus Subscriber
  • 2,727 posts

Posted 08 April 2009 - 12:32 PM


Another golden rule of thumb is: whenever you are feeding a pump from particular vessel, vortex breaker is considered more than desirable - not to say mandatory.


#4 ARAZA

ARAZA

    Gold Member

  • Members
  • 80 posts

Posted 08 April 2009 - 12:52 PM

Zauberberg,

May I dare to disagree with your statement. The necessity of vortex breaker depends on the type and the capacity of the pump being utilized and also on the suction line, whether it feeds the pump from the bottom or from the side of the tank.

Most of the small capacity pumps and the pumps getting suction from the side of the tank, vortex may not be an issue hence there is no requirement of the vortex breakers.

Best Regards,

ARAZA


QUOTE (Zauberberg @ Apr 8 2009, 12:32 PM) <{POST_SNAPBACK}>
Another golden rule of thumb is: whenever you are feeding a pump from particular vessel, vortex breaker is considered more than desirable - not to say mandatory.



#5 Zauberberg

Zauberberg

    Gold Member

  • ChE Plus Subscriber
  • 2,727 posts

Posted 08 April 2009 - 01:28 PM


You are absolutely right, Araza. I have never seen vortex breakers on side-nozzles; swirling is not possible to happen on lateral suction connections.
My comment was related to the most common arrangement, when pump is located beneath the suction vessel.

#6 chemicalkannan

chemicalkannan

    Junior Member

  • Members
  • 14 posts

Posted 08 April 2009 - 09:52 PM

JoeWong
Thank you for your valuble comments.now am under stand.and also once again thanks for all of you
kannan

#7 Dacs

Dacs

    Gold Member

  • Members
  • 393 posts

Posted 13 April 2009 - 08:04 PM

QUOTE (chemicalkannan @ Apr 8 2009, 01:31 PM) <{POST_SNAPBACK}>
Hi Friends

am Working in EPC Company.Currently We are doing Crude oil Tank Farm Projects. in this Project am doing Detail Engineering.my dought is The PMC is mentioned Data sheet ,the necessity of vortex breaker is determined by detailed engineering contractor.how can i find the vortex breaker is required or not.

by
kannan

Edited since I didn't read the previous posts and my post is only a duplication of what they said.

Move along smile.gif