We typically have a weep hole/drain in the low end to let rain, etc. drain out. I know some consider it a requirement to keep bird's nests, insects out etc. and install weather caps.
API 520 has a note that a "Weather cap may be required" but I could not find a reference on when it is "required."
ASME 1998 Section VIII Div. 1, UG-136(a)(9)(

The reverse of this question would also be helpful. If you use a weather cap, do you use a weep hole/drain?
Our applications are for primarily flammable vapors but overfilling could cause a liquid liquid solvent release. So much for the differences between vapor only service conditions and liquid conditions.
Several of our installations seems to be belt and suspenders and we have the weep hole and the cover. But now some PSV's are being flagged by the PSM group as not having the rain caps per API 520 even though they have the weep holes.
Any definitive sources on when you MUST have a rain cap?