Can someone give me the correct calculation for estimating the pressure drop along a 300m length of natural gas line.
The inlet pressure is 500mbarG.
The capacity needs to be 1100 Nm3/hr.
The proposed pipe size is 6".
|
Posted 16 February 2015 - 07:09 AM
Can someone give me the correct calculation for estimating the pressure drop along a 300m length of natural gas line.
The inlet pressure is 500mbarG.
The capacity needs to be 1100 Nm3/hr.
The proposed pipe size is 6".
Posted 16 February 2015 - 09:45 AM
Dear Lethal83,
You can review the textbook, Branan, Rules of Thumb for Chemical Engineers, in Fluid Flow: Compressible Flow.
Regards,
Napo.
Posted 16 February 2015 - 04:08 PM
lethal 83,
Enjoy the reading.
The pressure drop should be less than 100 mbars , my calculation 78 mbars considering CH4 , T=20C ,Z=1 , viscosity ;0.011 cp , CS pipe , absolute rugosity 0.2 mm .
http://checalc.com/s...PipeSizing.html
Good luck.
Breizh
Edited by breizh, 18 February 2015 - 01:38 AM.
Posted 16 February 2015 - 11:39 PM
Lethal83,
You might also wish to refer below link.
http://www.cheresour...p-correlations/
Regards.
Ajay S. Satpute
Posted 17 February 2015 - 02:39 AM
A very useful bit of knowledge to apply for low pressure gas flow calculations is that for situations where the pressure drop is less than approximately 10% of the absolute upstream pressure, you can use the equations for incompressible flow and still get good accuracy. The equations for incompressible flow are simpler than those for compressible gases and if you are doing the calculations by hand this can save a bit of effort. Here is an example calculation comparing the two methods for air, with a bit more discussion, and where you can see some real numbers.
You have to do the calculation under the assumption of incompressible flow to get the pressure drop, and then compare the calculated pressure drop with the upstream absolute pressure to decide if the calculation is valid. Because pipes are available only in discrete sizes you are really selecting between 4", 6" and 8" pipes in this case and the differences between the pressure drops in these pipe sizes are huge compared with the inaccuracy caused by the incompressible assumption if you stay within the 10% rule of thumb.
Tank Blanketing With Natural Gas/ Vapor Recovery SystemStarted by Guest_MethanolPlant_* , Today, 08:17 AM |
|
|
||
Flash Steam Vessel SizingStarted by Guest_JohnFields343_* , 24 Apr 2024 |
|
|
||
Pump Sizing ConsiderationsStarted by Guest_panagiotis_* , 07 Apr 2024 |
|
|
||
Barometric Legs Line SizingStarted by Guest_panagiotis_* , 17 Mar 2023 |
|
|
||
Sizing Of Vertical/horizontal Flash DrumStarted by Guest_Mohammad3799_* , 10 Mar 2024 |
|
|