Dear Experts,
I am currently sizing a relief valve for a liquid-liquid extraction column for fire case. Some key information are listed below:
- The LLE column is liquid full. It is a tall tower, with around 30m in T/T length
- The extract (mostly organics) comes out at the tower overhead. Heat of vaporization is around 300 kJ/kg
- The raffinate (mostly aqueous) comes out at the tower bottoms. Heat of vaporization is around 1500 kJ/kg
In the event of a fire, the bottoms portion will mostly be the one experiencing the heat flux from the external fire. However, since the column is liquid full, I imagine the tower to have an immediate heat transfer via convection/conduction from the heavy raffinate to the light extracts, with the overhead extracts being the first to vaporize at the top of the column (after preliminary expansion of course) before any vaporization of the bottoms occur. Thus, I plan to calculate the relief load based on the heat of vaporization of the extract (dHvap = 300kJ/kg).
I'd like to ask if this is a safe method to take, or is it overly conservative? Is there something else that could happen aside from what I imagine.
PS: I have read API 521 but it doesn't have any specific discussion on this type of problem.
Warm regards,
Luis