If a PSV being sized for pressure relieving equal to set pressure, the PSV (bigger in size) theoretically would be opened, without any overpressure in its upstream, till source of overpressure is removed. But the PSV may practically be operated in unstable manner due to probable flactuations in set pressure which easily affects balancing situation of the PSV in relieving condition.
Now looking at another view: when the vessel reach the set pressure and the PSV begins to lift, pressure is being relieved, so vessel internal pressure is going to be decreased but at the same time source of the overpressure is pressurizing the vessel! Then if PSV lifting has to be continued the system pressure must increase. For this reason the PSVs are allowed having an overpressure, let say 10%, to reach full lift. This experimental 10% margin for overpressure in ASME code is relatively small and conservative in safety standpoint, because up to 1.3-1.5 times of the design pressure yield stress wouldn't be exceeded and on the other hand such overpressure most likely would occur no more frequently than the hydrostatic test.
Thus, the PSV would be sized based on the same set pressure but with 10% (16% for multiple and 21% for fire) overpressure then relieving pressure to be 110% of the set pressure in PSV balancing situation and will lead to the smaller PSV and stable operation (without chattering and ....).
Edited by fallah, 27 February 2014 - 01:49 AM.