Hi Everyone,
To begin I am an engineer with only 2 years of practical experince which means I just have enough experience and education to make me dangerous but to my credit I know to check and double check and defer to the more experienced regarding sizing of equipment. OK this is what I would like some help with for those whom are willing...
I have an appliction that requires a heat pump to reject ~800,000 BTU/hr to an evaporator (using the heat rejected by the condenser to heat a process evaporator). The heat pump (screw compressor) quoted had a 600 BHP motor for the screw compressor using R142b as a refrigerant. OK something is not correct! I would expect (using hysterics) that the size is off by about 10 magnitudes!
Here are my quick calcs for everyones reference. Am I off in my assertions?
Heat Source 110 F (Process Condenser - Tin)
Heat Delivered 180 F (Process Evaporator - Tout)
Co-efficient of Performance (COPhp) = Qout/Win;
Ideal Carnot-cycle heat pump related to heat delivery temperature and temperature lift:
COPhp = Tout / (Tout - Tin) = (180+460) / (180-110) = 9.13
Assuming actual COPhp is 70% of ideal = 9.13 * 0.70 = 6.3
Evaporator Duty (Qin) = 0.75 MM btu/hr
Win = Qin / (COP -1) = 0.142 MM btu/hr; 297 kW per MM btu/hr
Win = 42.2 kW (this seems more reasonable to me for the compressor)
Qout = Qin + Win = 0.892 MM btu/hr (amount of energy we would need to provide via an alternate source)
Any help with this from you that deal with heat pumps would be appreciated.
Also I am sure the community could use some sizing tips and calcs from you because my searches on this sight left me with nothing.
Thank you
Edited by geoneo, 23 June 2014 - 10:09 AM.