Anyone can tell me the reason that pressure safety valve (PSV) is usually equipped with a bypass valve but thermal relief valve (TRV) is not.
Thanks in advance.
Edited by Hoang Nguyen, 04 September 2014 - 01:09 PM.
|
|
Posted 04 September 2014 - 01:05 PM
Dear all,
Anyone can tell me the reason that pressure safety valve (PSV) is usually equipped with a bypass valve but thermal relief valve (TRV) is not.
Thanks in advance.
Edited by Hoang Nguyen, 04 September 2014 - 01:09 PM.
Posted 04 September 2014 - 02:44 PM
Hi,
At first it should be noted that considering a by pass line around either PSV or TSV isn't the requirement of any standard/code and only can be seen in some engineering practices as recommendation that a by pass is to be suggested for PSVs.
Actually, a by pass line around a PSV might be hepful for relevant equipment purging or depressurizing during maintenance while considering that a TSV is a small size valve (normally 3/4" * 1") with very low liquid relief due to thermal expansion appears mentioned operations in maintenance case wouldn't be so applicable for a pressurized liquid filled equipment/pipe segment on which a TSV has been installed only for protection against over pressure due to thermal expansion... Then it's a normal practice not considering a by pass line for a TSV...
Posted 04 September 2014 - 08:32 PM
I get it. Thank you so much Sir. ![]()
Thermal Relief Valve For A Fire CaseStarted by Guest_QuantumEng_* , 19 Nov 2025 |
|
|
||
Minimum Distance Between Blowdown Valve And Cold Vent Outlet In A HighStarted by Guest_AMINEBELAL_* , 15 May 2026 |
|
|
||
Sizing Fire Case Relief Valve Installed Below Liquid LevelStarted by Guest_processrock_* , 14 Apr 2026 |
|
|
||
Two Phase Reverse Flow -Psv Sizing For Check Valve Failure CaseStarted by Guest_namita.modak1_* , 01 Apr 2026 |
|
|
||
Help Needed –Valve Causing High Pressure In Downstream VesselStarted by Guest_Alaa55_* , 27 Nov 2025 |
|
|