With reference to the above posts regarding API standard 2000. I have a copy of the fifth edition printed in april 1998. Regarding the expression given for venting requirements in metric units, I think that the latent heat should be expressed as J/kg not kJ/kg...anyone disagree?

#2 JoeWong

JoeWong

    Gold Member

  • ChE Plus Subscriber
  • 1,223 posts

Posted 29 January 2007 - 03:15 AM

QUOTE (niallmacdowell @ May 8 2006, 07:12 AM) <{POST_SNAPBACK}>
With reference to the above posts regarding API standard 2000. I have a copy of the fifth edition printed in april 1998. Regarding the expression given for venting requirements in metric units, I think that the latent heat should be expressed as J/kg not kJ/kg...anyone disagree?



Dear niallmacdowell,

I am in agreement with you if you refer to API 2000, 5th ed., Apr. 1998, page 8. The latent heat should be J/kg.

In addition, the Wetted Surface Area, section 4.3.3.2.1, under SI unit table, it should be "(square meter)" instead of "(square mm").

Hope you agree with me.

Best regards,

JoeWong

#3 proinwv

proinwv

    Gold Member

  • ChE Plus Subscriber
  • 391 posts

Posted 31 January 2007 - 09:58 AM

In Nov. 1999, API published an errata for formula 1B, page 8 as well as formula 5B, page 20 stating the units on "L" to be J/Kg.