how do I calculate a size of a vessel if I need 1 m3/s air flow at 13 barg for 30 seconds from the vessel?I dont have dynamic simulation SW, only the steady state. Thank you
Posted 10 May 2017 - 02:27 AM
Posted 10 May 2017 - 06:07 AM
The main issue you have is that you have three variables to define:
- Initial volume.
- Initial pressure.
- Final pressure
And from that infinite number of combinations you have to select the vessel based on a criteria you have to define.
Soy you have to remove 30 m3 from the vessel and end up with a pressure above 13 barg.
So, roughly (assuming isothermal, what is not true because the temperature will be decreasing as you remove gas and you have to calculate it), you can have:
- a 30 m3 vessel at 14.5 barg that ends at 13.5 barg
- a 15 m3 vessel at 15.5 barg that ends at 13.5 barg
- a 7.5 m3 vessel at 25 barg that ends at 21 barg
- a 3.75 m3 vessel at 25 barg that ends at 17 barg
And you can go on and on and on....
So the problem is not calculating (that is basic thermodynamic) but defining the selection criteria.
Posted 10 May 2017 - 08:27 AM
I dont know the initial volume. I only know I need to remove 1 m3 every second for 30 seconds from the vessel. How did you calculate the volumes please? Is it true I need 10.5 m3 vessel at 15 barg that ends at 11 barg?
Posted 10 May 2017 - 03:38 PM
No, if it ends at 11 barg you cannot remove air at 13 barg
As I said, you have to assume or define a vessel volume and that will give you the pressure needed.
Of you can define the initial vessel pressure and calculate the volume needed.
There is no single criterion.
In fact, you can also use a battery of air cylinders at 150 barg from a compressed gas supplier too, but those will go quite cold if you depressurize in 30 seconds.
All the examples are that you need 30 m3/s at normal conditions. If they are actual 30 m3/s at 13 barg, then you have to adjust the volumes accordingly.
Flash Steam Vessel SizingStarted by Guest_JohnFields343_* , 24 Apr 2024 |
Rapid Depressurization Of WaterStarted by Guest_golegolegole_* , 31 Mar 2024 |
Time Required To Heat Up A Fluid In A VesselStarted by Guest_panagiotis_* , 24 Jan 2023 |
Let Down Vessel In Methanol ProcessStarted by Guest_Manue_* , 21 Mar 2024 |
Vessel & Tank Liquid InternalStarted by Guest_Danish John Paul_* , 03 Jan 2024 |