we have many cases in our plants of installation indirect heaters in trunk lines and at oil processing plants inlet. the supplier of indirect heaters sometimes supplied it with thermal expansion safety relief . i want to know when this safety relief is mandatory to install and when it is not mandatory because some other suppliers supplied indirect heaters without this PSV. and what the reference for install or not install that PSV?

thanks very much



#2 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,954 posts

Posted 30 November 2018 - 03:31 AM

Mido:


 

In general when the fluid being heated is blocked in and the heating fluid is still flowing...



#3 Chemitofreak

Chemitofreak

    Gold Member

  • Members
  • 291 posts

Posted 30 November 2018 - 03:41 AM

Liquid thermal expansion over pressure can occur, when a system that contains a liquid is blocked in and the heat is gained from the environment (solar) or from the process. This causes the liquid to heat up and expand. If the liquid is confined, this expansion can result in over pressure.
 
One has to take into consideration the amount of liquid that can be trapped in between two valves for specifying the thermal relief valve.

Edited by Chemitofreak, 30 November 2018 - 03:45 AM.


#4 mido

mido

    Veteran Member

  • Members
  • 48 posts

Posted 01 December 2018 - 03:26 AM

Thanks for reply but my concern is about the need of safety relief if if the indirect heater have only manual isolation valves and not have automated shutdowns ...... can we remove this psv and control this hazard by administrative control that (in case of heater isolated to drain it). as this project is upgrade to existing system and to connect PSV to flare is not feasible.  



#5 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,954 posts

Posted 01 December 2018 - 05:36 AM

Thanks for reply but my concern is about the need of safety relief if if the indirect heater have only manual isolation valves and not have automated shutdowns ...... can we remove this psv and control this hazard by administrative control that (in case of heater isolated to drain it). as this project is upgrade to existing system and to connect PSV to flare is not feasible.  

 

In general, administrative control cannot be used instead of a PSV for overpressure relief...



#6 asantosa

asantosa

    Brand New Member

  • Members
  • 3 posts

Posted 19 March 2019 - 09:51 AM

Hello, interesting this topic reagrding on the volumne of the fluis that it is blocked; but actually, I´ve never found volume criteria of the fluid  that is trapped? FOoinstance, if the volume is higher than 50 liters, do I hace to install a TRV, no matter the classification of the fluid is ? ( inflamable, or toxic, etc ). This criteria shall be applied in interconnecting lines outside of batttery limit  or tanckage areas, but actually I do not know the volume or pipe lenght to be applied...Does anyone has heard about criteria for this? thanks



#7 Chemitofreak

Chemitofreak

    Gold Member

  • Members
  • 291 posts

Posted 22 March 2019 - 02:17 AM

@ Asantosa:

 

It can vary from company to company. In our company it is considered as 500 Liters



#8 breizh

breizh

    Gold Member

  • Admin
  • 6,347 posts

Posted 22 March 2019 - 04:00 AM

@ Asantosa,

 

Consider the link underneath.

 

https://www.eng-tips....cfm?qid=171158

 

Breizh 



#9 samayaraj

samayaraj

    Gold Member

  • Members
  • 239 posts

Posted 22 March 2019 - 06:38 AM

@ Asantosa,

 

Consider the link underneath.

 

https://www.eng-tips....cfm?qid=171158

 

Breizh 

 

Great thread! Mr. Art has given excellent point in choosing ball/ plug valve with self venting hole.