Hydraulics(Line Sizing)
hydraulics (line sizing) piping process engineering oil and gas
14 replies to this topic
#1 Lorean
Lorean
  • 16 posts
Posted 14 July 2020 - 02:00 PM
I have to size line system, firewater system. I have several questions. I have default sizing datasheet. 1)-do we add valve, fittings length to the pipe length? Do we add hydrant lenght, pipe branch length to the pipe length? In datasheet i have special fitting sections, so i ll add valves there for pressure drop. But should i add the valves length to the total length?2) - I have excell datasheet, and there i can only calculate every line individually. How can i size whole system?how to interconnect them, please help.
#2 Bobby Strain
Posted 14 July 2020 - 06:24 PM
Take a look at Harvey Wilson's software. You shouldn't use spreadsheets that have not been validated and approved by your company.
#3 Lorean
Lorean
  • 16 posts
Posted 14 July 2020 - 09:11 PM
Thanks Boby. Its indeed approved by my company. So should i add the branch length of the same pipe to the overall length? And should i add valve length too?
#4 breizh
  • 7,061 posts
Posted 14 July 2020 - 11:33 PM
Hi Lorean,
It's difficult to support you without knowing the detail of your work and how the calculation is done .
To me you should have the pipe length and equivalent length of pipe corresponding to the valves and other fittings . All together will be the total length of the line .
I've attached an example of network calculation using excel .
note : don't duplicate the posts . better to delete the ones in excess.
Hope this is helping you.
Edited by breizh, 14 July 2020 - 11:35 PM.
#5 Lorean
Lorean
  • 16 posts
Posted 15 July 2020 - 02:09 AM
Breith, tha k you a lot for your attention and time. Yes, i have pressure drop for fittings. Do i have to add branches from the main line to the line overall length?
#6 Lorean
Lorean
  • 16 posts
Posted 15 July 2020 - 02:14 AM
So there is main line(trunk), and there are several branches on the line. Should i include the length of these branches to the pressure drop calculation? Or i have to consider only main line length and fittings pressure drop? Thanks
#7 breizh
  • 7,061 posts
Posted 15 July 2020 - 03:52 AM
Branches are different lines , you need to perform calculation line per line , the connecting point being the nods .
Breizh .
#8 Lorean
Lorean
  • 16 posts
Posted 15 July 2020 - 07:05 AM
Breizh, thank you so much for detailed and quick replies :)
Edited by Lorean, 15 July 2020 - 07:07 AM.
#9 katmar
katmar
  • 705 posts
Posted 15 July 2020 - 08:16 AM
If the design needs to be accepted by your insurance company be aware that many insurers insist on firewater systems being designed using the Hazen-Williams model.  This model is not as accurate or flexible as the Darcy-Weisbach formula that process engineers normally use.  When I have had to design these systems I have done it in duplicate - using Darcy-Weisbach to satisfy myself that it will work and then again with Hazen-Williams to satisfy the insurers.
#10 Lorean
Lorean
  • 16 posts
Posted 15 July 2020 - 08:39 AM
Katmar, thanks a lot :) i ll research about it further :)
#11 breizh
  • 7,061 posts
Posted 15 July 2020 - 08:48 AM
https://www.canuteso...ler-system.html
Attached a link where you can find pointers to support your work.
#12 Lorean
Lorean
  • 16 posts
Posted 17 July 2020 - 01:09 AM
Breizh, thank you for your kind attention and time, i have read it, its veey informative :)
#13 gegio1960
gegio1960
  • 518 posts
Posted 17 July 2020 - 02:10 AM
Just to add that the big engineering company where I used to work, requests Hazen-William only for Cooling Water lines, not for Fire Water.
good luck!
#14 breizh
  • 7,061 posts
Posted 17 July 2020 - 11:16 PM   Best Answer
To add to my previous answers a standard for reference .
#15 Lorean
Lorean
  • 16 posts
Posted 20 July 2020 - 09:41 AM
Thanks everyone for taking time to reply :)