Methanol Level Decrease After Every Shipment Unloading.
#1
Posted 12 November 2021 - 09:40 PM
I hope to get some suggestions from you all. I handle Cryogenic Ethylene liquid. Ethylene liquid is vaporized using methanol vaporizing system. Ethylene is being unloaded into our storage tank by ship. After every shipment we face decrease in level of methanol in methanol vapourizer.
Methanol is used in 3 heat exchangers.
One- to vaporize ethylene liquid,
Two- to superheat the vapourized ethylene vapours
Three - to heat the Boil off gas from the storage tank (Boil off gas is compressed and sent to downstream plant along with ethylene vapours from vapouriser)
Here, No leak in methanol system is found.
Pressure of ethylene is higher than methanol pressure in 1 and 2 Heat exchangers. So methanol wont escape into 1 or 2 Heat exchanger, if there is leak in bundle of HE.
Only suspect is heat exchanger 3. But even if there is a leak inside, why level decreases only after shipement.
Please enlighten me.
#2
Posted 12 November 2021 - 09:48 PM
#3
Posted 13 November 2021 - 06:09 AM
Ill share system running parameters too.
Not sure what you mean by that.
One or more P&ID's showing the whole methanol system would however be required.
#4
Posted 16 November 2021 - 10:12 PM
1. It will happen when the shipment procedure is running because at that time there is a peak of pressure.
2. Detecting a leak in the methanol system has to be done by pressure test when i could be possible to do
3. Just to be sure, make a Methanol analysis to the ethylene after the shipment
4. A P/ID will be useful to understand the process
Horacio
Similar Topics
Interface Level In Hysys DynamicsStarted by Guest_CHEMSTRONG_* , 20 Apr 2022 |
|
![]() |
||
Natural Gas Saturator In Methanol ProductionStarted by Guest_Ranue_* , 18 Apr 2022 |
|
![]() |
||
Steam Methane Reformer In Production Of Methanol From Natural GasStarted by Guest_adam123collings_* , 01 Mar 2022 |
|
![]() |
||
![]() Moving Pump From 2Nd Floor To Ground Level ConsiderationsStarted by Guest_99CHE_* , 08 Mar 2022 |
|
![]() |
||
Level Control In Vba ExcelStarted by Guest_Divid Kelin_* , 07 Feb 2022 |
|
![]() |