Hi All,
We were trying to implement APC at Naphtha Hydrotreating Unit (NHT) at Stabilizer column. However, during Step-Test for MVs we have seen inconsistent behavior at column profile. Every Step test has a different gain which makes it hard to finalize the model. We tried to run many APC post models resulted of those step tests in a trial to control Stabilizer column but we failed to achieve stabilization as a minimum requirement.
Process Description: unstabilized hydrotreated Naphtha enters Stabilizer C-8131 it is heated in Stabilizer Feed/ Bottoms Exchanger E-8132 through E-8137 by heat exchange with the stabilized Naphtha from C-8131. The Stabilizer column bottoms are splitted into two streams. The bottom product stream is routed to Naphtha Splitter unti (NSU) through the feed/bottom exchangers under flow control. This flow control is cascaded to C-8131 bottom level control. The other stream goes for reboiling. This reboiling stream is further splitted into two. One goes to the stabilizer fired reboiler heater F-8131(approximately 62%) and the other to the Splitter reboiler heater F-8240(approximately 38%) convection section under heater pass flow control. The outlet from both heaters are combined and fed back to the stabilizer column. 81-PC-2100A is Furnace fuel gas pressure controller for F-8131 where this controller will regulate the fuel gas valve 81-PCV-2100A based on final temp required by TRC 81TC2075.
Overhead vapours from C-8131 are condensed in E-8138, further cooled in E-8139 and the condensate is collected in V-8133.A part of the overhead liquid is pumped back to C-8131 as reflux and the product is pumped to the Gas Tail Unit (GTU).
The NHTU Stabilizer is having a very large reflux to distillate ratio (more than 10 times). The reflux drum (V-8133) level controller (81LC2023) is manipulating the distillate flow (81FC2027), and the top tray temperature controller (81TC2035) is manipulating the reflux flow (81FC2025). A small percentage adjustment of reflux flow by the temperature controller will result in a large percentage change in the distillate flow, since the level control will need to adjust the distillate to compensate the change in reflux to control the level. This kind of control scheme is normally called the (direct) energy balance control scheme.
Examples of the issues;
- If I keep RefluX controller 81FC2025 in Auto and Reboiler Fuel gas controller 81PC2100A in Auto control without changing any set point, I will expect the column profile won't change majorly. Unfortunately, after few minutes the tray temp 81TC2035 will start ramping up without a clear reason!
- During 22nd Sept step test, STAB reboiler FG controller was taken on Auto “81PC2100A” and SV was increased by 0.05 barg & fixed. After this step, pressure increased in column “81PC2052” as well as BTM temp increased “81TC2075” and reached a temporary steady state. After few minutes of steady state, again BTM temp 81TC2035 increased drastically and pressure too without any change in reboiler FG opening valve!
- On 18th Sept, we tried to test reflux controller on MANUAL where opening was reduced by 1%. The tray temp 81TC2035 increased from 106 C to reach about 118 C until Panel Operator (PO) intervened to stop this increasing.
- Keep in mind, if we increase reboiler temp, the OVHD pressure will drop in this column while reflux flow will increase.
We have plenty of unclear behavior for this column where it supposes to be simple and direct model ! Please advise.