Please could you help me with a dilemma over the use of check valves (non-return valves) as the relief valve on a tank. Any comments on where they could be applied and how appropriate they are would be welcome.

One instance where I have seen them used is where the equipment is normally operated under vacuum.

I have also seen them located on a storage tank kept under a low pressure nitrogen blanket.

I am concerned as to what is or isn't appropriate. Particularly if the storage tanks are rated as pressure vessels.

#2 sahas

sahas

    Brand New Member

  • Members
  • 7 posts

Posted 07 November 2003 - 01:30 PM

As a secondary device a spring loaded check valve may acts as vauum relief. However by code this cannot be a primary safety device as listed in the overpressure protection report for the specific system if a storage tank is rated as Pressure vessel.

Section VIII Div 1 does not address on vacuum releif valves.

Please refer to API 2000 for Atmospheric /Low Pressure storage tanks

Hope this helps

#3 Guest_storry_*

Guest_storry_*
  • guestGuests

Posted 12 November 2003 - 05:48 AM

Thank you for the reply.

Could a check valve be used as a secondary pressure relief valve. For instance if it is set to lift a a pressure below that of the main bursting disc.

#4 Guest_Ben Thayer_*

Guest_Ben Thayer_*
  • guestGuests

Posted 12 November 2003 - 09:29 AM

Yes, as a "secondary device" you may have a check valve in addition to the main rupture disc or relief valve.

Most tanks have some type of "device" to allow for normal "breathing" when filling/emptying the tank. Depending on the nature of the material being stored, these devices may be pad/de-pad nitrogen regulators or conservation breather vents.

But having a regulator set to maintain 6" w.c. or having a check valve with 0.5 psi cracking pressure does not mean you don't need a relief device.

I would not characterize the check valve as a relief device but as just another piping component.