Hi all! I'm new here and this is going to be my first post. Is there anyone here who knows if there's a rule of thumb regarding the ratio of the cooling tower capacity with respect to the chiller's? Say, if I already know that my chiller's capacity should be 100TR, what would approximately be my cooling tower size? Thanks in advance!
|
|
Cooling Tower Sizing Rule Of Thumb
Started by santarosa, Nov 05 2007 10:14 AM
2 replies to this topic
Share this topic:
#1
Posted 05 November 2007 - 10:14 AM
#2
Posted 05 November 2007 - 07:48 PM
That's really small.
100 tons of refrigeration x 12,000 Btu/h/TR = 1,200,000 Btu/h
Delta (and probably others) carry standard products that will handle that.
See this link
100 tons of refrigeration x 12,000 Btu/h/TR = 1,200,000 Btu/h
Delta (and probably others) carry standard products that will handle that.
See this link
#3
Posted 06 November 2007 - 05:02 PM
If you go to:
http://www.chillers....eParameters.htm
You can find a sizing table that shows the normal process chiller guidelines for chillers and cooling towers used primarily in the plastics industry. Blow molding, injection molding, and extrusion are the main plastics uses for needing a chiller system.
Water Chillers, of course, are used in a lot of other industries, and this estimate is for the plastics industry:
- 95 oF Entering Water Temperature to tower
- 78 oF ambient Wet Bulb
- 3 GPM / Ton = water circulation rate
- 15,000 BTU / HR / Ton heat dissipation
- Consult Manufacturer for other conditions
In most cases the process chiller efficiency is based on the evaporator tons rather than condenser tons.
If you have a different application and a specific refrigerant, I would simply make a heat and mass balance around the chiller and calculate the condenser heat duty – which is by far the largest heat load.
Similar Topics
Sizing Fire Case Relief Valve Installed Below Liquid LevelStarted by Guest_processrock_* , 14 Apr 2026 |
|
|
||
Two Phase Reverse Flow -Psv Sizing For Check Valve Failure CaseStarted by Guest_namita.modak1_* , 01 Apr 2026 |
|
|
||
Steam Carrying Liquid From The Sour Water Stripping TowerStarted by Guest_kaidlut_* , 12 Sep 2024 |
|
|
||
Free Pump Sizing Calculator For Preliminary Engineering ChecksStarted by Guest_Gonoklab_* , 16 Mar 2026 |
|
|
||
Conceptual Sizing Of Adsorber ColumnStarted by Guest_JJvdM_* , 24 Oct 2019 |
|
|

FB