In determine capacity credit for relief valve sizing (ie. credit for flows out of the system), API 521 states "No credit should be taken for any favorable instrument response.”
My question is if a control valve would tend to move to a more closed position during the relief event, is it acceptable to take any capacity credit for flow through this control valve? I have discussed this question with our company's safety engineers and their response is that it is company practice to take credit for the flow through this valve based on its final steady state position, even though the valve may MOMENTARILY reduce the flow out of the system to less than the final steady valve, perhaps even to zero flow. I was advised that this is normal industry practice.
My opinion is that this not in accordance with API 521. Based on the following logic:
1. For the case where the control valve used for capacity credit would tend to open during the relief event (ie. where the valve position is controlled by pressure control on the upstream portion of the flow path out of the system), we would, of course, not take credit for this valve opening more and letting more flow through the valve as this would be taking credit for a favorable (good) instrument response. We would conservatively assume that the valve was in a position which would relieve the minimum flow (ie. valve at its original position).
2. Conversely, for the case where the valve would tend to close during the relief event (ie. where the valve position is controlled by pressure control on the downstream portion of the relief path – back pressure controlled, see attached example valve V-3), we can only ensure there will be flow through this valve if there is a good (favorable) control response. A good (favorable) control response would prevent the valve from going fully (or nearly) closed. If the control response is poor, the valve may go fully or nearly closed during the relief event. However, taking credit for the good control response goes against API 521. Even with a properly tuned controller, for the case of a back pressure controller, the flow out of valve would need to be at sometime less than the initial normal flowrate (as well as final steady state flow) in order to re-establish the same initial pressure. Furthermore, the final steady position of the valve may be such that it is barely open and would be outside of its steady state control range (ie. less than 5% open), thereby increasing the likelihood the valve may fully close momentarily.
3. Hence to comply with API 521, my opinion is that credit should not be taken for valves that tend to close (ie. moved to a more closed position) during the relief event as good (favorable) control response is required to prevent the valve from going fully closed or reducing the flow to less than the final steady state flow.
I would like to get the opinion of others on this issue and with regards to what is normal industry practice.