I'm thinking there's a simple explanation for this apparent conflict, but after searching for the answer I'm stumped. Can anyone shed some light on this?
Here's the issue…….
•The heat input equation is the same (Q = 21,000A^(0.82)) in OSHA and API 2000. That's the NFPA-30 equation that was adopted by OSHA, and therefore used in API 2000.
•The basis for determining exposed surface area is the same in OSHA and API 2000. It's based on NFPA-30 rules.
•But, the environmental factors in API 2000 are different. OSHA uses the NFPA30 F factors, consistent with it's use of the NFPA heat equation and surface area. The API 2000 factors can be much lower, resulting in a much lower heat input from the fire….. That's the apparent OSHA violation.
OSHA 1910.106 Flammable and combustible liquids
1910.106 b.2.v.f
The required airflow rate of subdivision © or (e) of this subdivision may be multiplied by the appropriate factor listed in the following schedule when protection is provided as indicated. Only one factor may be used for any one tank.
0.5 for drainage in accordance with subdivision viib of this subparagraph for tanks over 200 square feet of wetted area.
0.3 for approved water spray.
0.3 for approved insulation.
0.15 for approved water spray with approved insulation.
NFPA-30 (2008 ed) 22.7.3.5
(1) A reduction factor of 0.5 shall be allowed for tanks with wetted area greater than 200 ft2 (19m2) that are provided with drainage that meets the requirements of 22.11.1.
(2) A reduction factor of 0.3 shall be allowed for tanks that are protected with a water spray system that meets the requirements of NFPA 15, Standard for Water Spray Fixed
Systems for Fire Protection, and that are provided with drainage that meets the requirements of 22.11.1.
(3) A reduction factor of 0.3 shall be allowed for tanks that are protected with an automatically actuated water spray system that meets the requirements of NFPA 15, Standard
for Water Spray Fixed Systems for Fire Protection.
(4) A reduction factor of 0.3 shall be allowed for tanks protected with insulation that meets the requirements of 22.7.3.8.
(5) A reduction factor of 0.15 shall be allowed for tanks that are protected with a water spray system that meets the requirements of NFPA 15, Standard for Water Spray Fixed Systems for Fire Protection, and that have insulation that meets the requirements of 22.7.3.8.
API 2000
See Table 4 in attached file.