Dear Mr. Fallah,
Thanks a lot for your comment and guidance.
The superimposed back pressure in the flare network is negligible. The only thing that flows to the flare at normal condition is a very small purge gas flow rate (~7 SCFH, there is a purge reducer) and hence superimpised back pressure is almost 0. There are only two storage tanks (1000 bbl) connected to flare and the value that I provided for the back pressure is based on the full flow from all wells (outbreathing+flashed gas) and so we don't need to consider the effect of second tank.
I don't have the vendor datasheet but let me ask this in a more general way. I just would like to know if the overpressure is higher than 10% of the set point but the total pressure (set pressure + overpressure) is still below the design pressure of the tank/vessel do we need to necessarily pick balanced below relief valve style? I would like to know the answer for both PSVs and PVRVs.
(For PSVs for example, we know that back pressure of 21% is accetable for fire case because we can go to 121% of the vessel design pressure (21% back pressure => 21% accumulation). But lets assume an imaginary case that we set the PSV at the 80% of the vessel design pressure and the back pressure is 25% of the set point. Now the summation of back pressure and set point is exactly same as design pressure (100% of the design pressure and we should be OK! (25% back pressure => 25% accumulation). In other words, although the back pressure is 25% of the setpoint but the total pressure at relieving condition is less than 110% of the vessel design pressue)
It is appreciated if you shed some light on this.
Thanks,
Amin