Some additional info aiming at clarifying created queries:
1. Probability for a check valve to fail to open is 0.0009 /year, versus 0.0005 /year for a spring operated PSV (rough results from TNO CPR 12E, 1997). So check valve failure to open is probably a non credible contingency. Even so, corrossion may increase mentioned probability.
2. Once we assumed 304L for wet Natural Gas pipes containing ~20% CO2, a check valve may deserve 316L; but this is a duty of corrosion Engineer (Process does not have this duty here) and also depends on any other impurities (or solids) contained in the gas. Nevertheless corrossion risk will not be limited to check valve but will extend downstream as long as wet CO2 exists.
3. Will be a catastrofic failure, if the check valve sticks closed? This could be assessed by one knowing well the operation of upstream column removing CO2 (available data does not indicate that such failure would happen).
4. Even for an acceptable check valve on the branch to flare header, the original question is whether this is needed. Role of it would be to prevent (or at least limit) backflow from flare header to washing column (retaining CO2). Is there a case when pressure in flare header can be higher than pressure in washing column? If so, a check valve could be justified. No relevant data is given, probably there cannot be such a case. This would have to be assessed by the local team with your explanations.
Edited by kkala, 13 November 2010 - 06:10 AM.