1. As an example, blow down sizes and valves could be as follows for a 60 ton/h steam boiler (41 Barg, 400 oC).
Continuous blow down (max 10%) line 1” upstream control valve, 3” downstream. of it. Cv of the control valve (size 1”) about 4.5 (about 3.0 required for max controllable flow, 0.5 for minimum).
Discontinuous blow down line 4”, only with manual valves, without control valve. It seems that much higher flow is instantaneously needed by the discontinuous blow down to flush the boiler.
Continuous blow down comes from steam drum, discontinuous from steam and mud drum. I would expect blow downs to come from mud drum.
2. Concerning valve sizing under flashing, C. R. Branan (Rules of thumb for chemical Engineers, Gulf 2002) specifies max ΔP effective in producing flow (max allowable ΔP for sizing purposes). I understand that actual Cv is used. Higher ΔP would not produce more flow due to flashing.
This might be worth trying, understood as a short method of choked flow through valve (like an orifice) and downstream pressure separately (as said in previous post).