Three Percent Rule
#1
Posted 14 August 2007 - 02:44 PM
I'm a university student working as a summer intern at a refinery. I was just wondering if there's a creditable source (API Standard, manufacturer's handbook, etc.) that mentions the three percent rule. Is it just a rule of thumb or is it actually published somewhere? I've tried doing a google search and a search in Crosby's Pressure Relief Valve Engineering Handbook but have come up empty.
As I understand it, the three percent rule is a guideline that states that the pressure drop in the inlet piping to the PSV must be less than 3% of the vessel's relieving pressure. It is meant to prevent chattering and subsequent damage to the relief valve.
Thanks in advance,
Nate
#2
Posted 15 August 2007 - 05:36 AM
References:
1. ASME Section VIII, Appendix M
2. API RP520 Part II - Installation, 5th Ed., August 2003
#3
Posted 28 August 2007 - 12:09 AM
References:
1. ASME Section VIII, Appendix M
2. API RP520 Part II - Installation, 5th Ed., August 2003
Dear Phil,
1.Why the value is fixed on "3%"?Why not a lower or higher value?In the other hand I am interested of knowing about the origin of "3%" value.
2.Should we calculate the non-recoverable losses based on "rated capacity" of PSV?If yes as you know this value should be specified by VENDOR,so what approach the designer should follow?Should He/She hold the sizing of inlet line to psv up to the supply of data from vendor or it is possible to apply a rough margin to calculated relieving load and obtain the rated capacity?
3.Is the 3% rule applicable for inlet line to blowdown valves?
Thanks in advance.
#4
Posted 28 August 2007 - 05:42 AM
The flow rate to use in calculating the inlet line pressure drop is the PSV rated (stamped) capacity. As the Process Engineer, you are responsible for sizing the PSV. Your company probably has one or two vendors they deal with so you can choose the vendor and model of PSV your company tells you to use. With the vendor, model and size now known, you then get the stamped capacity of the PSV directly from the vendor cataloge.
The 3% Rule applies to spring operated, pop-open PSVs.
#5
Posted 28 August 2007 - 06:13 AM
#6
Posted 04 September 2007 - 09:07 AM
In calculation of inlet line pressure drop,should we consider the density value at winter conditions?
Cheers.
#7
Posted 04 September 2007 - 12:17 PM
#8
Posted 04 September 2007 - 04:13 PM
CORRECTION!!!

This is what happens when your mouth goes before the brain. You use the conditions at SET PRESSURE, whatever that may be. NOT RELIEF.
#9
Posted 04 September 2007 - 11:42 PM
CORRECTION!!!

This is what happens when your mouth goes before the brain. You use the conditions at SET PRESSURE, whatever that may be. NOT RELIEF.
But I think that using the conditions at relief seems to be more logical.

#10
Posted 05 September 2007 - 06:15 AM
That's the way it is.
#11
Posted 05 September 2007 - 08:59 PM
Again, sorry for cut-in...
jprocess,
PSV will open at setpressure, pressure possible accumulate upto 110% of setpressure (non-fire case).
Let review the effect of pressure on flow (hence inlet line loss) with selected PSV orifice area
Effect 1 : Lower pressure ==> Lower density ==> larger volumetric flow (with same mass flow) ==> Higher inlet line loss
Effect 2 : Lower pressure ==> Lower DP (less significant on critical flow) across PSV ==> lower driving force ==> Lower flow ==> Lower inlet line loss
Maximum inlet line loss may/may not at setpressure nor Relieving conditions.
If you use rated flow (based on higher DP) will properties obtain from setpressure, then it will be conservative.
I would recommend you to conduct a little more studies to convince yourself (prove my comments), the best would publish you results here for benefits of all.
Just a little extra on Phil's statement "The 3% Rule also applies to pilot operated PSVs.", Phil statement is correct. However, you may have exception if the pilot line tapping is located elsewhere i.e. vessel. Refer to API RP 520 Pt II, section 4.2.
I would encourage you to read "Using the ideal gas specific heat ratio for Relief-valve Sizing", CE, Nov 2003, by Aubry SHACKELFORD. This effect will be more significant in sizing PSV and as well as inlet line loss.
JoeWong

#12
Posted 06 September 2007 - 05:42 AM
You're reading too much into why the API Committee says to use set pressure for the 3% Rule. As a note, there is discussion about changing it to relief conditions instead. We are only talking about a 3% (+ or -) pressure loss, not a very significant change to vapor/gas desnisy in the scheme of things. As a matter of fact, the 3% Rule also applies to liquid flow where there is not only no density change but you still aren't supposed to take into account static head; doesn't sound very conservative to me. And your statment, "If you use rated flow (based on higher DP) will properties obtain from setpressure, then it will be conservative." confuses me. you are supposed to use the PSV rated (stamped) capacity in the calculation wheather you use the set pressure or not so there is no additional conservatism introduced.
In your brief review of the effect of pressure on flow with a selected orifice size, your Effect 1 is basically negligible and your Effect 2 to me is non-existent. It isn't less significant on critical flow; it is no significance on critical flow. And what driving force across the PSV?
So I stand by my statement, "What logic?"
#13
Posted 07 September 2007 - 02:45 AM
Thanks for knocking my head to think more...
You may be right that i read too much into it. However question raised by my young engineers really push me to read and think more into it so that my statement / judgment is convincing.
Moreover, your second statement already shows that API committee still in discussion on which conditions to be used.
Most peoples aware that 3% rule is just a guideline to comply but it still can be deviated. I personally has deviated at least once (upto 4.5%) but selected a PSV with high blowdown in order to maintain the margin between opening & closing of PSV. So the 3% rule really is not strictly needs to be comply and one may exceed if one understand the background on the margin.
I remember in one of your post, you mentioned that 3% rule does NOT include the static head. I have not put much thought on this issue. I do agree (prelim) as margin loss on the line pressure drop during PSV opening, you will gain it back when the PSV is closing / reseating. I think i should put extra thought on this subject.
In your brief review of the effect of pressure on flow with a selected orifice size, your Effect 1 is basically negligible and your Effect 2 to me is non-existent. It isn't less significant on critical flow; it is no significance on critical flow. And what driving force across the PSV?
Yes. This may create some confusion to certain level.
My starting point is ....a PSV will open at setpressure, pressure possible accumulate upto 110% of setpressure (non-fire case). Those the properties at 100% setpressure to 110% setpressure will be different (i agree it may be insignificant).
At 100% setpressure, density lower, higher pressure drop is expected with same mass flow.
At 110% setpressure, density increases, lower pressure drop is expected with same mass flow.
Thus lower density, higher volumetric flow, which probably result higher pressure drop.
At 100% setpressure, the driving force across a PSV (selected) orifice will be 100% minus backpressure (subcirtical flow) or Critical pressure (generally 50-55% of PSV inlet pressure)
At 110% setpressure, the driving force across a PSV (selected) orifice will be 110%* minus backpressure (subcirtical flow) or Critical pressure (generally 50-55% of PSV inlet pressure)
* to be exact we may need to minus inlet line loss
If we go in detail, we may find that driving force for 110% case is slightly higher which potential gives higher flow across PSV. High flow will cause higher inlet line loss.
Increasing pressure ==> increase density ==> increases volumetric flow ==> less pressure drop
Increasing pressure ==> increase driving force across PSV ==> increase flow passing PSV ==> higher pressure drop
Thus, maximum inlet line loss may/may not at setpressure nor Relieving conditions.
If one use properties at setpressure (lower density), calculate rated flow considering PSV inlet is at 110% set pressure (higher driving force), then probably the inlet line loss will be conservative. This scenario is not a feasible scenario but just built in the conservatism.
Write upto here...looks like a bit confuse...i would like some of you to point out mis-concept if any...
Anyway, i have done some studies years ago, the pressure drop is not so significant whether you use set pressure condition or relieving condition.
The consideration of "using ideal K for sizing PSV" is really give significant flow different as compare to using set pressure condition or relieving condition to determine the PSV rated flow.
Any of you who is reading this post, i would encourage you to read the findings in "Using the ideal gas specific heat ratio for Relief-valve Sizing", CE, Nov 2003, by Aubry SHACKELFORD.
JoeWong

#14
Posted 11 September 2007 - 08:14 AM
The 3% rule is met on essentially all new installations.
On existing installations, we try real hard to meet the 3% rule. If there are good reasons and it is exceeded, there's extra documentation to inform and archive the reasons and the blowdown must be adjusted. No matter what, inlet dP must not exceed 5%.
#15
Posted 04 June 2009 - 01:21 AM
i'm a student, currently interning at a refinery. I have been reading about this topic and would like to know the consequences if this 3% rule is not obeyed.
I have read Merkblatt AD-A2 and ISO 4126 which requires the the implementation of this 3 % rule. but I have also been told, that these guidelines are optional, BUT in a way a company is taking a risk by not adhering to these guidelines.
what if implementing the 3 % rule is not possible in real situation? (as far as i have been told, costs to enlarge/shorten/adjust pipings and also pilot operated valves are very expensive) Other than chattering, what else can possibly occur if the 3% rule is not obeyed?
I have also read from a source(which I have forgotten to write down), that with more than 3% pressure drop in the inlet pipe an overpressure could occur in instruments. Is it true? Is it caused by the pressure accumulating in the instruments, not being able to overcome the large pressure drop in the pipeline?(self-derived solution.if this is not the case, appreciate a further explanation.)
Lats but not leas, what are the 'good reasons' and where can i view the documentations mentioned above. And why 5%?
Appreciate any help I can get!
#16
Posted 04 June 2009 - 07:19 AM
Last I heard, API commissioned a study to look into the 3% rule and revise it if possible.
We take the same appraoch as latex with our installtations-all new installations are 3% or less, and retrofits try to get below 3% if possible-and never above 5%. Anything above 3% gets extra attention, particularly to the manufacturers stated blowdown values.
The other thing I would mention is that for pilot valves, the 3% rule applies to the sensing lines for flowing-type pilots; for non-flowing types API 520 Part II paragraph 4.2.3.2 recommends lines with a flow area of 0.07 sq. in. (45 sq. mm).
#17
Posted 04 June 2009 - 07:23 AM
Appreciate any help I can get!
Normally,all types of PSVs are fitted with a blowdown adjustment ring set at 5%.
If pressure drop of inlet line exceeded 3%,let say 5%,when relieving to be started the pressure sensed by PSV is to be equal to blowdown pressure and would be closed without complete relieving and following that chattering would be happened.
If we have to have inlet pressure drop higher than 3%,we shall adjust blowdown with higher value,let say 7%,and at this time the pressure drop could be up to 5%.
#18
Posted 20 June 2009 - 10:12 AM
Appreciate any help I can get!
Normally,all types of PSVs are fitted with a blowdown adjustment ring set at 5%.
If pressure drop of inlet line exceeded 3%,let say 5%,when relieving to be started the pressure sensed by PSV is to be equal to blowdown pressure and would be closed without complete relieving and following that chattering would be happened.
If we have to have inlet pressure drop higher than 3%,we shall adjust blowdown with higher value,let say 7%,and at this time the pressure drop could be up to 5%.
I think 3 percent is necessary for PSV body lifetime. because is more higher pressure drop of inline, the PSV will fast to open and to stop which will damage the body.
#19
Posted 23 June 2009 - 12:23 AM
I guess what you inferred was the CHATTERING.
#20
Posted 09 March 2010 - 01:44 PM
I realise it is an old article, but in it Leung presents an equation (Eqn 55) that is used later in the article to calculate the max inlet line length for a given ID assuming the maximum 3% inlet line losses:
dPinlet = 0.03(Pset - Pback)
P in absolute pressure
i.e. the allowable inlet line pressure drop is limited to 3% of the absolute set pressure less the psv absolute back pressure.
I realise the wording in API 521 Part II, section 4.2.2 is quite specific "...the pressure-relief valve should not exceed 3 percent of the set pressure of the valve..." but I can see where he is coming from. Is there any merit in this approach for conventional PSVs (i.e. not balanced bellows or pilot operated PSVs)?
If so, would Pback not have to be the superimposed back pressure at the rated flow rather than the static back pressure used in the PSV sizing equations?
#21
Posted 18 March 2010 - 08:45 AM
1 - The 3% rule applies to the stagnation pressure NOT just pressure, which includes kinetic energy
2 - The rule exists to prevetn "chatter" and potential "self destruct" of the relief valve - pressure rises to set pressure, pressure drop from flow cause pressure to drop at valve throat, relief valve reseats, pressure rises, relief valve lifts - rinse and repeat

As a side effect the valves capacity will be severely reduced and a much higher overpressure will be required to keep the valve open
Similar Topics
Floating Head Rule For Shell And Tube ExchangerStarted by Guest_Ghasem.Bashiri_* , 06 Dec 2023 |
|
![]() |
||
![]() Is There Any Rule Of Thumb For Estimation Of Steam Generation From FirStarted by Guest_AnbIran_* , 20 Nov 2023 |
|
![]() |
||
10/13 Rule ApplicationStarted by Guest_Alex1_* , 28 Apr 2023 |
|
![]() |
||
Rule Of Thumbs - Concept DesignStarted by Guest_kangas_* , 12 Jan 2021 |
|
![]() |
||
High Pressure Spherical & Bullet Storage RuleStarted by Guest_Vibha_101_* , 15 Sep 2020 |
|
![]() |