We have a solvent storage tank of 60m³. Recently there has been a modification done to prevent vapor venting to atmosphere during offloading of tanker as required by regulations.
The modification is the PVRV(pressure vacuum relief valve) outlet(from the positive pressure side) is routed back to the tanker vapor space via a flame arrestor to equalize the pressure and prevent any vapor venting to atmosphere during tanker offloading into the tank.
The PVRV pipe to the tanker has two manual valves and they remain closed when the tank is in operation. This leads to the tank being isolated and unable to vent(breathe out) if there is a pressure rise. The credible scenario of any pressure increase can be due to a fire, or excessive ambient temperature. The max ambient temperature is 32°C.
The solvent properties are:
IBP=175°C
vapor pressure=0.07kPa @ 20°C
Flash point (TCC)= 51°C
LEL =0.6%V
CAS number=64741-65-7
Is there a standard stating there should not be isolation valves downstream of a PVRV?
What if the PVRV malfunctions or flame arrestor gets blocked Can this lead to a undesired high pressure in tank during offloading?
I want to suggest to route the piping upstream of the PVRV back to the tanker as this will make the PVRV independent and also equalize the pressure during tanker offloading.
Your expert advice is solicited