Multiple Psvs To Avoid Chattering


This topic has been archived. This means that you cannot reply to this topic.
9 replies to this topic
Share this topic:
| More

#1 Guest_distill_*

Guest_distill_*
  • guestGuests

Posted 29 April 2009 - 01:25 AM

I am sizing a PSV for new fees KO drum , operating pressure 22 barg and set pressure is 24.15 barg. Since the operating and set pressure is very close , I am selecting the valve type as Pilot Operated.
My design contingency is blocked outlet for which the orifice required is L type. There are few other governing contingencies like control valve failure and fire etc for which the relieving rate is very small and as this ratio with reference to blocked outlet is less than 25% (vapor service) , there is probability of chattering so I have to apply 2 PSVs with staggered settings (one @DP and 2nd @105%). Orifices are now K and F. Per API 521 max allowable overpressure for multiple valves is 16% , in that case the smaller PSV set pressure will be DP*1.16 and bigger PSV max allowable overpressure will be DP*1.16/Set Pressure.

My question is that what is the advantage of putting 2 psvs to avoid chattering as they both can open at some overpressue at which both PSV are seeing the same relieving pressure?

#2 Art Montemayor

Art Montemayor

    Gold Member

  • Admin
  • 5,782 posts

Posted 29 April 2009 - 05:25 AM


Distill:

A normal PSV works successfully in accordance to its design capacity and how close it discharges that same design rate. In other words, it wants to discharge the flow rate it was designed to handle. It is a dumb device in that if you don’t furnish enough fluid flow rate, it will open excessively and cause a relatively over-reaction to the need for relief. When it behaves in this manner, it “chatters” – i.e., it opens and shuts in rapid, successive responses because it has excess relieving capacity. Of itself, this is not a bad situation for making sure that relief is taking place. What is bad is that the repetitive opening and closing of the valve’s plug and orifice can cause physical damage to the valve itself and ruin it’s ability to control a relief situation. That is bad.

What is normally done to alleviate the situation is what you are contemplating: install TWO PSVs. However, the capacity of the PSVs combined is the total relief load. In other words, the capacity of each PSV is approximately ½ of the total load. Now, the second PSV will only kick in and relieve when the capacity of the first is used up and it can’t handle anymore fluid, causing the system pressure to start to increase. If sized appropriately, this arrangement will eliminate any chattering and still give you 100% protection for your worse scenario. However, the trade-off is that the PSV cost will be greater and so will their maintenance.


#3 djack77494

djack77494

    Gold Member

  • ChE Plus Subscriber
  • 1,282 posts

Posted 29 April 2009 - 08:46 AM

If this is truly a problem, an alternative approach is to utilize a regulating PSV. Such a PSV is a bit more costly and functions more like a self contained control valve. It would open (relieve) in proportion to the degree that the pressure exceeds the design pressure. Such a valve should not be subject to "chattering".

#4 Guest_distill_*

Guest_distill_*
  • guestGuests

Posted 29 April 2009 - 09:34 PM

Thanks Art and Djack,

Djack,
My client doesn't have any experience with modulating pilot operated relief valve and they dont want to try it now else that was my suggestion.

Art,
I sized my PSVs the same way you also suggested. My only worry is that since the relief pressure (set+allowable overpressure) is same when I am discharging the small rates (small PSV), at some point (I can't do dynamic analysis though), based on the overpressure that point the bigger valve might start opening while the small valve is not fully opened yet - then the bigger valve will start chattering (rate will be less than 25% criterion). Am i missing something?

#5 Qalander (Chem)

Qalander (Chem)

    Gold Member

  • ChE Plus Subscriber
  • 829 posts

Posted 29 April 2009 - 11:19 PM


Dear

I understand that the pop pressure should never exceed the design pressure,thus the 1.16*Design pressure should not be the VALUE

rather this might be Design Pressure/1.16 or some other appropriate figure. Other learned colleagues will jump in to guide indeed.

#6 jerald04

jerald04

    Junior Member

  • Members
  • 17 posts

Posted 30 April 2009 - 07:19 PM

Distill,

Apologies but may I digress from the intended topic for a while please?

You made a statement "Since the operating and set pressure is very close , I am selecting the valve type as Pilot Operated".

Can you explain further on this?




#7 maldini

maldini

    Junior Member

  • Members
  • 15 posts

Posted 01 May 2009 - 12:38 AM

Dear jerald04 as the ratio between operating pressure and set pressure = or higher than 90 % it is recommended to use pilot safety valve as per API

Dear Distill
can u give me more details for your case and as I understood that your is blockage two phase (25% vap, and 75%liquid ) if u use dier method for sizing psv I don’t know from where chattering will occur


#8 Guest_distill_*

Guest_distill_*
  • guestGuests

Posted 02 May 2009 - 12:28 AM

Hi Qalander (Chem),

You are correct that PSV will pop at the set pressure but it will be fully opened at the relieving pressure which is 1.16*DP in this case (Overpressure/accumulation).

Hi maldini,

No, my PSV discharge is not two phase (its vapor release to flare); what I meant to say that if your PSV governing contingency required flow rate is X kg/hr and, for some other design contingency Y kg/hr, then if ratio of Y/X is less than 25% than chattering can happen per standard desing practices.
I am trying to avoid this and using 2 PSVs with staggered settings.

#9 Qalander (Chem)

Qalander (Chem)

    Gold Member

  • ChE Plus Subscriber
  • 829 posts

Posted 02 May 2009 - 10:55 AM


Thanks distill,

May I humbally suggest that if the contents to be depressurised are not very small in quantity then the consideration for keeping pop pressure lower is better

as otherwise the vessel (or any other containment enclosure in question) will remain subjected to higher than design pressure and
thus may yield stresses to a higher degree; sort of making the conditions dangerous.

Hope this is somewhat helpful.

#10 JoeWong

JoeWong

    Gold Member

  • ChE Plus Subscriber
  • 1,223 posts

Posted 09 May 2009 - 08:53 AM

Distill,
All discussion still remain qualitative and conceptual level.

Can you please provide detail information about the relieving flow, properties, set pressure, etc for both cases ? We may go a little bit detail to evaluate.