Jump to content



Featured Articles

Check out the latest featured articles.

File Library

Check out the latest downloads available in the File Library.

New Article

Product Viscosity vs. Shear

Featured File

Vertical Tank Selection

New Blog Entry

Low Flow in Pipes- posted in Ankur's blog

Pvsv And Thief Hatch-urgent


This topic has been archived. This means that you cannot reply to this topic.
7 replies to this topic
Share this topic:
| More

#1 Guest_Renoyd_*

Guest_Renoyd_*
  • guestGuests

Posted 01 June 2008 - 10:41 AM

Hello there,

A low pressure condensate storage tank (750bbl) with a thief hatch: 10", set at 8 oz (pressure) and 0.4 oz (vacuum). No blanketing system, do we need a PVSV additionally for truckout given relief load is known. i.e. the maximum truckout capacity. What else need to be considered?

Thanks in advance.

#2 Art Montemayor

Art Montemayor

    Gold Member

  • Admin
  • 5,782 posts

Posted 01 June 2008 - 07:28 PM

First of all, your terminology is used wrong; a thief hatch is not a relief valve. A thief hatch is nothing more than a nozzle with a blind flange (a "hatch") located on top of a hydrocarbon liquid tank. It is a left-over term from the days of yesteryear when condensate storage tanks were the targets of thiefs who would syphon out the fuel for use on their tractors, cars, or other vehicles. The hatch was used to measure the contents of the tank. This flanged nozzle could also be used today for an emergency relief valve or vacuum valve location.

You need to be specific. Just exactly what relief (both pressure and vacuum) do you have on your tank? If it is not blanketed, then what is the normal vapor space pressure in it? What do you do to/with this tank? Is it a field operation that uses routine tanker truck collection once or twice a week? We need more information in order to give some comments that make sense and don't waste our time as well as yours.


#3 Guest_Renoyd_*

Guest_Renoyd_*
  • guestGuests

Posted 01 June 2008 - 10:08 PM

QUOTE (Art Montemayor @ Jun 1 2008, 07:28 PM) <{POST_SNAPBACK}>
First of all, your terminology is used wrong; a thief hatch is not a relief valve. A thief hatch is nothing more than a nozzle with a blind flange (a "hatch") located on top of a hydrocarbon liquid tank. It is a left-over term from the days of yesteryear when condensate storage tanks were the targets of thiefs who would syphon out the fuel for use on their tractors, cars, or other vehicles. The hatch was used to measure the contents of the tank. This flanged nozzle could also be used today for an emergency relief valve or vacuum valve location.

You need to be specific. Just exactly what relief (both pressure and vacuum) do you have on your tank? If it is not blanketed, then what is the normal vapor space pressure in it? What do you do to/with this tank? Is it a field operation that uses routine tanker truck collection once or twice a week? We need more information in order to give some comments that make sense and don't waste our time as well as yours.


Art,

Thank you very much for your quick response.

This is an atmospheric tank as you can see from the set pressures of the thief hatch. Currently we don't have any relief valve on this tank. There is just a mushroom vent on the top. This will be a newly added tank to the field. We are asked to verify whether a PVSV is needed for the truckout operations. This tank is basically for condensate storage, and the truckout operations will be exactly what you assumed.

Any inputs will be appreciated.

Renoyd

#4 djack77494

djack77494

    Gold Member

  • ChE Plus Subscriber
  • 1,282 posts

Posted 02 June 2008 - 09:17 AM

Renoyd,
You have not heeded Mr. Montemayor's plea to use correct terminology. As he stated, a thief hatch is not a relief device and does NOT have a set pressure (positive or negative). A conservation vent (a.k.a. a PVSV) is commonly used on API650 atmospheric storage tanks; some type of venting capacity is a requirement of the codes.

I am further confused by your refering to the tank as if it is existing, but then saying it "will be a newly added tank". Which is it - new or existing? Also, what do you mean by a mushroom vent? Is this an open vent pipe that ends with a mushroom shaped cover, perhaps used to keep rain and dust from falling into the tank? If so, that is the provision that the original tank designer made for the tank's venting needs. Reiterating what Art has said, please provide complete information for a complete answer.

#5 Guest_Renoyd_*

Guest_Renoyd_*
  • guestGuests

Posted 02 June 2008 - 10:28 AM

Djack77494,

I appology if I made you confused, but I clearly stated it will be a newly added tank to the field, and we are still verifying the application of the PVSV. I have the data sheet of the tank here. It does state the set pressures of the thief hatch, and as Art indicated, thief hatch can indeed be used for emergency relief purposes.

The mushroom vent is like what you said, a vent pipe with mesh screen to prevent debris from entering inside, 10" size, no set pressure.

Regards,

Renoyd

#6 Guest_Renoyd_*

Guest_Renoyd_*
  • guestGuests

Posted 02 June 2008 - 01:33 PM

Just for clarification: the tank is designed to API-12F (modified). The thief hatch used is a spring-loaded pressure-vacuum relief hatch.

#7 Art Montemayor

Art Montemayor

    Gold Member

  • Admin
  • 5,782 posts

Posted 02 June 2008 - 03:32 PM

Renoyd:

Doug is right. What I said was "This flanged nozzle could also be used today for an emergency relief valve or vacuum valve location." I never said the hatch could be used for emergency relief purposes. There are many companies that sell PVSV for installation on existing "thief hatches". This nomenclature is merely traditional and means nothing as far as thieves are concerned. What I'm trying to establish is that we are talking about the same thing. We waste a lot of effort in just doing that - and don't get to the problem.

What you seem to have is an atmospheric pressure 12F API condensate tank for field installation. How you have a PVSV installed on it at the same time as you have an open, screened vent to the atmosphere is beyond me. You either have an atmospheric-vented tank or you have a closed, PVSV-protected tank. You can't have both -- one defeats the other. This is exactly the kind of erroneous information that we try to eliminate in order to generate sensible, logical, safe, and correct responses. In trying to guess what it is that you need, what I can say is:


If you want a closed tank, seal off the screened, open vent.

Ensure that the proposed PSVS (which you erroneously continue to call a thief hatch) is of the correct capacity to take care of your safe venting needs to atmosphere in BOTH pressure and vacuum modes. Do not forget that you also need emergency venting in the event of a fire or a "blow-through" case. I doubt the PVSV will be big enough to cover you in all these cases. I hope this helps.

#8 Guest_Renoyd_*

Guest_Renoyd_*
  • guestGuests

Posted 02 June 2008 - 10:04 PM

Thanks a lot. Art and Djack. They are helpful.




Similar Topics